Cause : Undervoltage comes when one of the following conditions was true when the drive was stopped and a Run command was entered:
• DC bus voltage dropped below the level specified in L2-05.
• Contactor to suppress inrush current in the drive was opened.
• Low voltage in the control drive input power. This alarm outputs only if L2-01 is not 0 and DC bus voltage is under L2-05.
- Phase loss in the drive input power.
- Check for wiring errors in the main circuit drive input power. Correct the wiring.
- Loose wiring in the drive input power terminals.
• Ensure the terminals have been properly tightened.
• Apply the tightening torque to the terminals as specified. - There is a problem with the drive input power voltage.
• Check the voltage.
• Lower the voltage of the drive input power so that it is within the limits listed in the specifications. - Drive internal circuitry is worn.
• Check the maintenance time for the capacitors (U4-05).
• Replace either the control board or the entire drive if U4-05 exceeds 90%. - The drive input power transformer is too small and voltage drops when the power is switched on.
• Check for an alarm when the magnetic contactor, line breaker, and leakage breaker are closed.
• Check the capacity of the drive input power transformer. - Air inside the drive is too hot. Check the temperature inside the drive.
- The CHARGE light is broken or disconnected. Replace either the control board or the entire drive.