Cause : Control Power Supply Voltage Fault comes when voltage is too low for the control drive input power. L2-02 changed from its default value in drive that is 7.5 kW or smaller without installing a Momentary Power Loss Ride-Thru.
- Correct the setting to L2-02 or install an optional Momentary Power Loss Ride-Thru unit.
- Control power supply wiring is damaged.
- Cycle power to the drive. Check if the fault reoccurs.
- If the problem continues, replace the control board, the entire drive, or the control power supply.