Cause : Undervoltage 3 (Soft-Charge Bypass Relay Fault) comes when the soft-charge bypass relay failed or the relay or contactor on the soft-charge bypass relay is damaged.
• Cycle power to the drive and see if the fault reoccurs.
• Check monitor U4-06 for the performance life of the soft-charge bypass relay.
• Replace either the control board or the entire drive if U4-06 exceeds 90%.