Cause : Overcurrent comes when the power unit has detected an overcurrent condition. If you're experiencing an overcurrent fault with a Yaskawa drive, it indicates that the current flowing through the motor exceeds the permissible limit set by the drive's protection settings.
"Overcurrent fault" in "Yaskawa drive" indicates that the current drawn by the motor has exceeded the drive's limit. This means the load on the motor is greater than the drive's rated capacity.
Common Causes of "Overcurrent Fault in Yaskawa drive"
1. Motor Overload:
- Mechanical Binding: Check if the motor is mechanically overloaded, or if the machine it drives is jammed.
- Incorrect Motor Parameters: Ensure that motor parameters (e.g., rated current, voltage, power) are correctly configured in the drive.
- Excessive Load: The connected load might be beyond the motor’s capacity, leading to excess current draw.
- Current Limit Settings: The drive may be set with incorrect current limits. Check the parameter for current limits (typically found in the drive’s configuration) and adjust if necessary.
- Acceleration/Deceleration Times: If the ramp-up or ramp-down time is too short, it can cause an overcurrent due to sudden changes in motor speed. Increase the ramp times to reduce the load on the drive.
- Drive Mode: Ensure the drive is in the correct operating mode for the application (e.g., V/f, vector control).
- Voltage Fluctuations: Voltage spikes or sags can cause the drive to draw more current. Ensure the input voltage to the drive is stable and within the specified range.
- Faulty Power Supply: If the power supply has issues such as phase loss or imbalance, it could cause an overcurrent fault.
- Poor Grounding or Loose Connections: Inspect all wiring connections for any loose or corroded contacts, as this can cause spikes in current.
4. Motor or Cable Issues:
- Motor Short Circuit: The motor windings may be shorted, which would cause the motor to draw excessive current.
- Cable Damage: Damaged or shorted motor cables can also cause overcurrent faults. Inspect the motor wiring for physical damage or insulation breakdown.
- Overheated Motor: If the motor is overheating, it could be causing higher current draw. Check for proper cooling and ambient temperature conditions.
5. Drive Fault:
- Internal Fault in the Drive: If the drive itself has internal damage or faulty components (like IGBTs), it could falsely report an overcurrent fault. The drive may need inspection or replacement.
- Control Board Fault: Check for potential issues in the control or power boards of the drive.
Diagnostic Steps:
Check Motor Load:
- Ensure the motor isn't overloaded. Manually rotate the motor or check the application to ensure there's no mechanical binding.
Verify Parameter Settings:
- Check the motor-related parameters such as current limits, acceleration/deceleration times, and voltage in the drive.
- Adjust the parameters gradually to see if it reduces the occurrence of the overcurrent fault.
Inspect Motor and Cables:
- Test the motor for shorts or insulation breakdown.
- Inspect the motor cables for damage or loose connections.
Monitor Drive Status:
- Use the drive’s diagnostic tools to monitor real-time current draw and error logs.
- Identify if there are any irregular current spikes during operation.
Test Components Separately:
- If possible, run the motor with a different drive to isolate whether the issue is with the drive or motor.