Yaskawa E7, G7, GA800 & GA500 Drive
174
Mar 20, 2024 10:46 am
Cause : Option Communication Error comes when the drive did not receive a signal from the controller or the communications cable wiring is incorrect.
- There is a short-circuit in the communications cable or the communications cable is not connected.
- Electrical interference caused a communication data error.
• Examine the control circuit lines, main circuit lines, and ground wiring, and decrease the effects of electrical interference.
• Make sure that a magnetic contactor is not the source of the electrical interference, then use a Surge Protective Device if necessary.
• Use only the recommended cables or other shielded line. Ground the shield on the controller side or the drive input power side.
• Separate the communication wiring from drive power lines, and install a noise filter to the input side of the power supply for communication.
• Decrease the effects of electrical interference from the controller. - The option is incorrectly installed to the drive.
- Correctly install the option to the drive.
- The option is damaged.
- If the fault continues and the wiring is correct, replace the option.