Yaskawa E7, G7, GA800 & GA500 Drive
217
Mar 20, 2024 10:50 am
Cause : Control Fault comes when motor parameters are set incorrectly Correctly set the motor parameters and do Auto-Tuning again.
- When A1-02 = 4 [Control Method Selection = Advanced Open Loop Vector], the drive takes long to ramp to stop because of these settings:
• The torque limit setting is too low.
• L3-11 = 1 [Overvoltage Suppression Select = Enabled].
• d5-01 = 1 [Torque Control Selection = Torque Control]. - When Rotational Auto-Tuning changes or the installation environment changes, make sure that you do Line-to-Line Resistance Tuning and set L8-20 = 0 [Control Fault & Step Out Detect = Disabled].
- The torque limit setting is too low. Adjust L7-01 to L7-04 [Torque Limit].
- The load inertia is too large.
- Adjust C1-02, C1-04, C1-06, and C1-08 [Deceleration Times].
- Set the frequency reference to the minimum output frequency, and stop the Run command when the drive stops deceleration.
- The drive is trying to ramp to stop a machine that cannot do ramp to stop or on a machine for which deceleration is not necessary.
- Line-to-line Resistance Tuning is not done.
- Do Stationary Auto-Tuning for Line-to-Line Resistance.