Yaskawa E7, G7, GA800 & GA500 Drive
496
Mar 19, 2024 11:30 am
Cause : Ground Fault comes when the ground fault current at the Inverter output exceeded approximately 50% of the Inverter rated output current.
- A ground fault occurred at the Inverter output. (A ground fault can be caused by motor burn damage, worn insulation, or a damaged cable.)
- short-circuit between +V, -V, and AC terminals occurred.
• Overload in the control circuit terminal - Reset the fault after correcting its cause.
Note: Before turning the power ON again, make sure that no short- circuit or ground fault occurs at the Inverter output. - Make sure that incorrect wiring has not been done.
• Check the resistance and wiring for the frequency setting potentiometer, etc. (Check that the current for terminals +V and –V is 20 mA or less.)