GF fault in yaskawa G7 drive

1 Posts
1 Users
0 Reactions
426 Views
Posts: 19820
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Ground Fault comes when the ground fault current at the Inverter output exceeded approximately 50% of the Inverter rated output current.

  1. A ground fault occurred at the Inverter output. (A ground fault can be caused by motor burn damage, worn insulation, or a damaged cable.)
  2. short-circuit between +V, -V, and AC terminals occurred.
    • Overload in the control circuit terminal
  3. Reset the fault after correcting its cause.
    Note: Before turning the power ON again, make sure that no short- circuit or ground fault occurs at the Inverter output.
  4. Make sure that incorrect wiring has not been done.
    • Check the resistance and wiring for the frequency setting potentiometer, etc. (Check that the current for terminals +V and –V is 20 mA or less.)