Cause : Overcurrent comes when the Inverter output current exceeded the overcurrent detection level. (200% of rated current). A short-circuit or ground fault occurred at the Inverter output. (A short or ground fault can be caused by motor burn damage, worn insulation, or a damaged cable.)
- The load is too large or the acceleration/deceleration time is too short.
• A special-purpose motor or motor with a capacity too large for the Inverter is being used.
• A magnetic contactor was switched at the Inverter output. - There is a break in the PG wiring.
- The PG is wired incorrectly.
- Power isn't being supplied to the PG.
- A short-circuit between +V, -V, and AC terminals occurred.
• Overload in the control circuit terminal. - Make sure that incorrect wiring has not been done.
• Check the resistance and wiring for the frequency setting potentiometer, etc.