Cause : Overcurrent comes when the Inverter output current exceeded the overcurrent detection level. (200% of rated current). A short-circuit or ground fault occurred at the Inverter output. (A short or ground fault can be caused by motor burn damage, worn insulation, or a damaged cable.)

  1. The load is too large or the acceleration/deceleration time is too short.
    • A special-purpose motor or motor with a capacity too large for the Inverter is being used.
    • A magnetic contactor was switched at the Inverter output.
  2. There is a break in the PG wiring.
  3. The PG is wired incorrectly.
  4. Power isn't being supplied to the PG.
  5. A short-circuit between +V, -V, and AC terminals occurred.
    • Overload in the control circuit terminal.
  6. Make sure that incorrect wiring has not been done.
    • Check the resistance and wiring for the frequency setting potentiometer, etc.

 