OH alarm code in yaskawa E7 drive
Cause : Heatsink Overheat comes when the temperature of the heatsink exceeded the overheat pre-alarm level. Cooling Fin/Cooling Fin Fan Overheat The temperature of the Drive cooling fin exceeded the temperature programmed in parameter L8-02.
Cooling fan(s) are not working, high ambient temperature, a heating unit in close proximity to Drive is present.
1. Surrounding temperature is too high.
• Check the surrounding temperature.
• Improve the air circulation within the enclosure panel.
• Install a fan or air conditioner to cool surrounding area.
• Remove anything near drive that may cause extra heat.
2. Internal cooling fan has stopped.
• Check for dirt build-up on the fans and cooling fan.
3. Airflow around the drive is restricted.
• Provide proper installation space around the drive as indicated in the manual.
• Allow for the proper space and ensure that there is sufficient circulation around the control panel.
• Check for dust or other foreign materials clogging the cooling fan.
• Clear debris caught in the fan that restricts air circulation.