Cause : Motor Overloaded comes when the motor overload protection function has operated based on the internal electronic thermal value.
- The load is too heavy. The acceleration time, deceleration time, and cycle time are too short.
- Check the size of the load and the length of the acceleration, deceleration, and cycle times.
- The constant setting for speed search is incorrect. (Motor overload occurred due to motor hunting and vibration.)
• Use the speed search function.
• Adjust the settings of the Speed search operating current (b3-02) and Speed search deceleration time (b3-03).
• Use the estimated speed search function. (Autotuning for motor line-to-line resistance is required.) - Motor overload occurred when running at low speed. (If a general-purpose motor is used, motor overload can occur when running at low speed even if running within the rated current.).
- Motor protection selection (L1-01) is set to general-purpose motor protec- tion (1) when an Inverter duty motor is used.
- The directions of the motor and PG are different. (Only in flux vector control)
• Correct the PG wiring.
• Correct the motor wiring.
• Change the setting of PG rotation (F1-05). - The V/f characteristics voltage is too high. Check the V/f characteristics.
- The Motor Rated Current (E2-01) is incorrect. Check the Motor Rated Current (E2-01).