Cause : Overtorque Detected 2 comes when there has been a current greater than the setting in L6-05 for longer than the setting in L6-06.
- Make sure that the current set- ting in L6-05 and time setting in L6-06 are appropriate.
- Check the mechanical system and correct the cause of the overtorque.