Cause : PID Selection comes when PID Control Setup Error. The following settings have been made at the same time: b5-01 (PID Control Method Selection) has been set to a value other than 0. b5-15 (PID Sleep Function Start Level) has been set to a value other than 0. b1-03 (Stopping Method Selection) was set to 2 or 3.
- Check parameters b5-01, b5-15, and b1-03 and correct the error.