Cause : Digital Output Selection Error- These two parameters are set at the same time:

• H2-60 ≠ F [Term M1-M2 Secondary Function ≠ Not Used]
• H2-01 = 1xx [Term M1-M2 Function Selection = Inverse output of xx]

Clear the H2-01 to H2-03 = 1xx [Inverse output of xx] settings.

These two parameters are set at the same time:
• H2-63 ≠ F [Term M3-M4 Secondary Function ≠ Not Used]
• H2-02 = 1xx [Term M3-M4 Function Selection = Inverse output of xx]

These two parameters are set at the same time:
• H2-66 ≠ F [Term M5-M6 Secondary Function ≠ Not Used]
• H2-03 = 1xx [Term M5-M6 Function Selection = Inverse output of xx]

These parameter pairs are set incorrectly:
• H2-21 [Comparator 1 Lower Limit] > H2-22 [Comparator 1 Upper Limit]
• H2-27 [Comparator 2 Lower Limit] > H2-28 [Comparator 2 Upper Limit]

1. Set parameters H2-21 ≤ H2-22.
2. Set parameters H2-27 ≤ H2-28.