Cause : DC Bus Overvoltage comes when the DC bus voltage exceeded the trip point. When a Yaskawa E7 drive displays a "DC Bus Overvoltage" alarm, it indicates that the voltage level on the DC bus of the drive has exceeded the acceptable threshold.
• 208-240Vac: Trip point is ≥ 400Vdc 480Vac: Trip point is ≥ 800Vdc
- Surge voltage present in the drive input power.
• Install a DC link choke or an AC reactor.
• Voltage surge can result from a thyristor convertor and a phase advancing capacitor operating on the same drive input power system. - The motor is short-circuited.
- Check the motor power cable, relay terminals and motor terminal box for short circuits.
- Correct grounding shorts and turn the power back on.
- Ground current has overcharged the main circuit capacitors via the drive input power.