Cause : Input Phase Loss (Main Circuit Voltage Fault) comes when the main circuit DC voltage oscil- lates unusually (not when regener- ating). This fault is detected if a load is greater than approximately 80% of the maximum motor capacity. This fault is detected when L8-05 is set to 1.
- An open-phase occurred in the input power supply.Â
- A momentary power loss occurred.
- The wiring terminals for the input power supply are loose.
- The voltage fluctuations in the input power supply are too large.
- The voltage balance between phases is bad.
- Reset the fault after correcting its cause.