Cause : DC Bus Undervoltage comes when the DC bus voltage is ≤ L2-05 208-240Vac: Trip point is ≤ 190Vdc 480Vac: Trip point is ≤ 380Vdc.
When one of the following conditions was true when the drive was stopped and a Run command was entered:
• DC bus voltage dropped below the level.
• Contactor to suppress inrush current in the drive was opened.
• Low voltage in the control drive input power.
- Phase loss in the drive input power.
- Check for wiring errors in the main circuit drive input power. Correct the wiring.
- Loose wiring in the drive input power terminals.
• Ensure the terminals have been properly tightened.
• Apply the tightening torque to the terminals as specified. - There is a problem with the drive input power voltage.
• Check the voltage.
• Lower the voltage of the drive input power so that it is within the limits listed in the specifications. - Drive internal circuitry is worn.
• Replace either the control board. - The drive input power transformer is too small and voltage drops when the power is switched on.
• Check for an alarm when the magnetic contactor, line breaker, and leakage breaker are closed.
• Check the capacity of the drive input power transformer. - Air inside the drive is too hot. Check the temperature inside the drive.