Cause : MC Answer- back(Inrush Prevention Circuit Fault) comes when a fault occurred in the surge prevention circuit. The magnetic contactor did not respond for 10 s even though the magnetic contactor ON signal has been output.
- The magnetic contactor in the main circuit failed.
- The magnetic contactor excitation coil is burned out.
- Try turning the power supply off and on.
- Replace the Inverter if the fault continues to occur.