Cause : Main Circuit Capacitor Neutral Point Potential Error comes when a loss in capacity due to aging of the main circuit capacitor or the Inverter parts are faulty.
- An open phase was detected for an output.
- Carrier frequency set value (C6-03, C6- 04) is unsuitable.
- Check the set values for C6-03 and C6-04.
- The maximum output frequency that can be set for 400 V Class Inverters is restricted by the carrier frequency setting.