Cause : Power Supply Overvoltage comes when The input power supply voltage became equal to or higher than the Input Power Supply Overvoltage Detection Level.
200 V Class: Approximately 277 Vac
400 V Class: Approximately 554 Vac
- The power supply voltage exceeded the range listed in drive input power specifications.
- Regenerative operation was performed when the power supply capacity was too small.
- The power supply circuit opened during regeneration.
- Reduce the voltage to within the range in the power supply specifications.
- Increase the capacity of the power supply.