Forum

Share:
Notifications
Clear all

AUv alarm code in yaskawa R1000 drive

1 Posts
1 Users
0 Reactions
215 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Power Supply Undervoltage comes when the input power supply voltage became equal to or lower than the Input Power Supply Undervoltage Detection Level.

1. 200 V Class: Approximately 150 Vac
2. 400 V Class: Approximately 300 Vac

  • The power supply voltage is low.
  • Increase the power supply voltage.
  • A phase loss occurred in the input power supply.
  • Check the input power supply for phase loss or an imbalance in the interphase voltages.
  • Investigate and correct the cause and reset the fault.
Share: