ndAT fault error code in yaskawa R1000 drive

1 Posts
1 Users
0 Reactions
272 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Model, Voltage Class, Capacity Mismatch comes when the drive from which the parameters were copied and the drive to which the parameters will be written have different electrical specifications, capacities, are set to different control modes, or are different models.

The device being used to write the parameters is blank and does not have any parameters saved on it.

  1. Make sure model numbers and specifications are the same for both drives.
  2. Make sure all connections are correct, and copy the parameter settings onto the USB Copy Unit or the operator.