Yaskawa FP605, P1000, D1000 & R1000 Drive
350
Mar 23, 2024 10:47 am
Cause : PID Control Selection Fault- These parameters are set at the same time:
• b5-01 = 1
• b5-11 = 1 [PID Output Reverse Selection = Negative Output Accepted] And one of these parameters is set:
• d2-02 ≠ 0.0 [Frequency Reference Lower Limit ≠ 0.0%]
• Y1-06 ≠ 0.0 [Minimum Speed ≠ 0.0%]
• Y4-12 ≠ 0.0 [Thrust Frequency ≠ 0.0%]
• Y1-01 ≠ 0 [Multiplex Mode ≠ Drive Only]
• YF-01≠ 0 [PI Aux Control Selection ≠ Disabled]
Correct the parameter settings.
• Y2-01 = 5 [Sleep Level Type = Output Frequency (non-PID)]
• Y2-02 [Sleep Level] > 0.0 Hz
• Y4-17 [Utility Start Delay Time] > 0.0 min