oPE16 fault error code in yaskawa FP605 drive

1 Posts
1 Users
0 Reactions
346 Views
Posts: 19965
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Energy Saving Constants Error comes when the Energy Saving parameters are not set in the applicable setting range. 

1. These parameters are set at the same time:
• b8-01 = 1 [Energy Saving Control Selection = Enabled]
• S1-01 = 1 [Dynamic Noise Control = Enabled]

2. Make sure that E5-xx is set correctly as specified by the motor nameplate data.

3. Disable Energy Saving Control or Dynamic Noise Control.