Cause : Power Supply Frequency Pre-Alarm comes when the input power supply frequency fluctuates more than ±15 Hz. The regenerative unit enters the baseblock state during pre-alarm. When the input supply frequency returns to normal conditions, the regenerative unit will release the base block and continue to operate.
- Momentary power loss has occurred.
- Activate the momentary power loss ride-thru.
- Voltage distortion is large.
- Increase the power supply capacity.
- Voltage detection failure .
- Phase loss has occurred.
- Confirm the power supply and regenerative unit is correctly connected.