Cause : Underload or Belt Break Detected comes when the output current decreased less than the motor underload curve set in L6-14 [Motor Underload Level @ Min Freq] for longer than the time set in L6-03 [Torque Detection Time 1].
- xThe belt has broken disconnecting the motor from the load.
- Examine parameters L6-13 [Motor Underload Curve Select] and L6-14.