dEv alarm code in yaskawa L1000A drive

1 Posts
1 Users
0 Likes
30 Views
Posts: 14785
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

Cause : Speed Deviation comes when the deviation between the speed reference and speed feedback is greater than the setting in F1-10 for longer than the time in F1-11.

  1. Load is too heavy Reduce the load.
  2. Accel/decel ramp is too short.
  3. Increase the acceleration and deceleration times (C1-01 through C1-08).
  4. The load is locked up.
  5. Check the machine.
  6. Parameter settings are inappropriate.
  7. Check the settings of parameters F1-10 and F1-11.
  8. The motor brake is not applied.
  9. Ensure the motor brake operates properly with a brake control command from the drive.