Yaskawa Z1000, L1000A, L1000E & V1000 Drive
192
Mar 28, 2024 5:01 am
Cause : Z Pulse Noise Fault Detection (CLV/PM control mode only) comes when the Z Pulse is out of phase by more than 5 degrees for 10 consecutive revolutions.
- Noise interference along the PG cable- separate the PG cable lines from the source of the noise.
- PG cable is not wired properly- rewire the PG encoder and properly ground all shielded lines.
- PG option card or the PG encoder are damaged- if the problem continues after cycling power, replace the PG option card or the PG encoder.
