dv2 fault code in yaskawa L1000E drive

1 Posts
1 Users
0 Likes
23 Views
Posts: 14785
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

Cause : Z Pulse Noise Fault Detection (CLV/PM control mode only) comes when the Z Pulse is out of phase by more than 5 degrees for 10 consecutive revolutions.

  1. Noise interference along the PG cable- separate the PG cable lines from the source of the noise.
  2. PG cable is not wired properly- rewire the PG encoder and properly ground all shielded lines.
  3. PG option card or the PG encoder are damaged- if the problem continues after cycling power, replace the PG option card or the PG encoder.