Yaskawa Z1000, L1000A, L1000E & V1000 Drive
275
Mar 28, 2024 5:02 am
Cause : Inversion Detection (CLV/PM control mode only) comes when the torque reference and acceleration are in opposite directions and the speed reference and actual motor speed differ by more than 30% for the number of times set to F1-18.
- The Z Pulse offset is not set properly to E5-11
- An external force on the load side caused the motor to move
• Make sure the motor is rotating in the proper direction.
• Identify and fix any problems on the load side causing the motor to rotate in the opposite direction. - Noise interference along the PG cable affecting the A or B pulse. PG encoder is disconnected, improperly wired, or the PG option card or PG encoder are damaged - properly rewire the PG encoder and connect all lines including shielded line.
- Rotational direction for the PG encoder set to F1-05 is the opposite of the motor line order- properly connect the motor lines for each phase (U, V, W).
- The drive incorrectly detected the position of the motor poles.
