dv6 fault code in yaskawa L1000E drive

1 Posts
1 Users
0 Likes
33 Views
Posts: 14785
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

Cause : Overacceleration Detection comes when the acceleration of the elevator car exceeds the overacceleration detection level (S6-10).

  1. The encoder offset needs to be adjusted whenever the encoder is replaced or when reversing the direction of the motor.
  2. Noise along the encoder cable.
  3. Cables for the motor encoder are not wired properly, or the PG option card (or the encoder itself) is damaged.
  4. Check the encoder wiring for any loose connections.
  5. Make sure that the shielded line is properly grounded.