Cause : Adjusted Slip Calculation Error comes when the Auto-Tuning results were not in the applicable parameter setting range.
- Make sure the input motor nameplate data is correct.Â
- Do Rotational Auto-Tuning again and correctly set the motor nameplate data.
- If you cannot uncouple the motor and load, do Stationary Auto- Tuning 2.