Cause : Auto-Tuning Error for PG-E3 Encoder Characteristics comes when the signal lines between the PG-E3 option card and encoder are disconnected at the R+ and R- terminals.
  1. Refer to the installation manual for the PG-E3 option card for information on correct connection of signal lines.
  2. Excessive electrical interference at the PG-E3 option card.
  3. The software for the PG-E3 option card does not support the Auto-Tuning of PG-E3 encoder characteristics.
  4. Check the software version (PRG) for the PG-E3 option card.
  5. The software version PRG: 1102 or later support Auto-Tuning of PG-E3 encoder characteristics.