Yaskawa Z1000, L1000A, L1000E & V1000 Drive
1
Posts
1
Users
0
Reactions
242
Views
Mar 29, 2024 8:02 am
Cause : Safe Disable Circuit Fault Signal (H1-HC, H2-HC) Release comes when one Safe Disable channel is open while the other one is closed. The signals to the Safe Disable inputs are wrong or the wiring is incorrect.
- Check signal status at the input terminals H1 and H2.
- If the Safe Disable function is not utilized, the terminals H1-HC, and H2-HC must be linked.
- One of the Safe Disable channels is faulty. Replace either the control board or the entire drive.