Forum

Share:
Notifications
Clear all

HbbF alarm code in yaskawa L1000E drive

1 Posts
1 Users
0 Reactions
242 Views
Posts: 18455
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Safe Disable Circuit Fault Signal (H1-HC, H2-HC) Release comes when one Safe Disable channel is open while the other one is closed. The signals to the Safe Disable inputs are wrong or the wiring is incorrect.

  1. Check signal status at the input terminals H1 and H2.
  2. If the Safe Disable function is not utilized, the terminals H1-HC, and H2-HC must be linked.
  3. One of the Safe Disable channels is faulty. Replace either the control board or the entire drive.
Share: