oFb02 fault code in yaskawa L1000A drive

1 Posts
1 Users
0 Likes
30 Views
Posts: 14785
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

Cause : Option Card Fault at Option Port CN5-B comes when same type of option card is currently connected or An option card of the same type is already installed in option port CN5-A.

  • This fault also comes when an input option card is already installed in option port CN5-A.
  1. Except for PG options, only one of each option card type can only be installed simultaneously. Make sure only one type of option card is connected.
  2. Install a communication option, a digital input option, or an analog input option. More than one of the same type of card cannot be installed simultaneously.