Yaskawa Z1000, L1000A, L1000E & V1000 Drive
181
Mar 29, 2024 7:47 am
Cause : Motor Overheat Alarm (PTC Input) comes when the motor overheat signal to analog input terminal A1, A2, or A3 exceeded the alarm detection level. Detection requires setting multi-function analog inputs H3-02, H3-10 to E.
- Check the size of the load, the accel/decel times, and the cycle times.
- Decrease the load.
- Increase the acceleration and deceleration times (C1-01 through C1-08).
- Adjust the preset V/f pattern (E1-04 through E1-10) by reducing E1-08 and E1-10.
- Do not set E1-08 and E1-10 too low. This reduces load tolerance at low speeds.
- Check the motor rated current.
- Enter the motor rated current to parameter E2-01 as indicated on the motor nameplate.
- Ensure the motor cooling system is operating normally.
- Repair or replace the motor cooling system.