oH4 fault code in yaskawa L1000A drive
Cause : Motor Overheat Fault (PTC Input) comes when the motor overheat signal to analog input terminal A1, A2, or A3 exceeded the fault detection level. Detection requires setting multi-function analog inputs H3-02, H3-10 to E.
  1. Check the size of the load, the accel/decel times, and the cycle times.
  2. Decrease the load.
  3. Increase the acceleration and deceleration times (C1-01 through C1-08).
  4. Adjust the preset V/f pattern (E1-04 through E1-10) by reducing E1-08 and E1-10.
  5. Do not set E1-08 and E1-10 too low. This reduces load tolerance at low speeds.
  6. Check the motor rated current.
  7. Enter the motor rated current to parameter E2-01 as indicated on the motor nameplate.
  8. Ensure the motor cooling system is operating normally.
  9. Repair or replace the motor cooling system.
