Cause : Motor Overheat Fault (PTC Input) comes when the motor has overheated or the temperature of the motor has exceeded the safe operating limit.

  1. Check the load level, acceleration/deceleration time, and motor start/stop frequency (cycle time). 
  2. Decrease the load.
  3. Increase the values [Acceleration/ Deceleration Times].
  4. Set E2-01 [Motor Rated Current (FLA)] correctly to the value specified by the motor nameplate. 
  5. Make sure that the motor cooling system is operating correctly, and repair or replace it if it is damaged. 