oL1 fault code in yaskawa L1000A drive
Cause : Motor Overload- When Yaskawa L1000A drive indicates a "Motor Overload" fault, it suggests that the current drawn by the motor has exceeded safe operating limits. This fault can occur due to various reasons, including mechanical issues, excessive load, or improper tuning of the drive parameters. Here's how you can address this issue:
  1. Immediate Action: If the motor overload fault occurs, stop the operation of the motor immediately to prevent damage to the motor or the drive.
  2. Reduce Load: Evaluate the load on the motor and ensure it is within the rated capacity of both the motor and the drive. Reduce the load if necessary to prevent overloading.
  3. Inspect Mechanical Components: Check the mechanical components of the system, including the motor, coupling, gearbox (if applicable), and load. Look for signs of mechanical binding, misalignment, or excessive friction that could lead to increased motor current.
  4. Review Motor Parameters: Check the motor parameters and configuration settings in the drive's setup. Ensure they match the specifications of the motor and are configured correctly for your application. Adjust parameters such as motor current limits and acceleration/deceleration rates if necessary.
  5. Check Feedback Devices: If the motor is equipped with feedback devices such as encoders or resolvers, verify their operation. Faulty feedback devices can lead to incorrect motor control and cause overloads.
  6. Inspect Cooling: Ensure that the motor is adequately cooled during operation. Overheating of the motor can lead to increased current draw. Check for proper ventilation and cooling of the motor and its surrounding environment.
  7. Verify Drive Parameters: Review the drive parameters related to motor control and protection settings. Adjust these parameters as needed to provide adequate protection while avoiding unnecessary trips.
