oPE04 alarm code in yaskawa L1000A drive

1 Posts
1 Users
0 Likes
22 Views
Posts: 14785
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

Cause : Terminal Board Mismatch Error comes when the drive, control board, or terminal board have been replaced and the parameter settings between the control board and the terminal board no longer match.

  1. Set A1-03 to 5550 to load the parameter settings stored in the terminal board to the drive.
  2. Initialize parameters after drive replacement by setting A1-03 to 2220 or 3330.