Cause : Analog Input Selection Error comes when a contradictory setting is assigned to multi-function analog inputs H3-02 or H3-10 and PI functions conflict.

  1. Change the settings to H3-02 and H3-10 so that functions no longer conflict.
  2. At least two analog input terminals are set to the same function (i.e., at least two of these parameters have the same setting: H3-02 or H3-10).
  3. The following simultaneous contradictory settings: H3-02 or H3-10 = C (PI Target Value) while b5-18 = 1 (enables b5-19 as the target PI value).
  4. Disable one of the PI selections.