oPE08 alarm code in yaskawa L1000A drive

1 Posts
1 Users
0 Likes
26 Views
Posts: 14785
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

Cause : Parameter Selection Error- You set a function has been set that cannot be used in the motor control method selected.

  1. Attempted to use a function that is not valid for the selected control mode.
  2. Check the motor control method and the functions available.
  3. In Open Loop Vector Control, n2-02 is greater than n2-03 Correct parameter settings so that n2-02 is less than n2-03.
  4. b1-14 (Phase Order Selection) is set to 1 (Switch phase order) when in using a PG option card.
  5. Correct the parameter settings.
  6. Use U1-18 to find parameters that are set outside the specified setting range. Other errors are given precedence over oPE08 when multiple errors occur simultaneously.