Cause : Parameter Selection Error- You set a function has been set that cannot be used in the motor control method selected.
- Attempted to use a function that is not valid for the selected control mode.
- Check the motor control method and the functions available.
- In Open Loop Vector Control, n2-02 is greater than n2-03 Correct parameter settings so that n2-02 is less than n2-03.
- b1-14 (Phase Order Selection) is set to 1 (Switch phase order) when in using a PG option card.
- Correct the parameter settings.
- Use U1-18 to find parameters that are set outside the specified setting range. Other errors are given precedence over oPE08 when multiple errors occur simultaneously.