oPE21 alarm code in yaskawa L1000A drive

1 Posts
1 Users
0 Likes
28 Views
Posts: 14785
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

Cause : Elevator Parameter Setting Fault comes when elevator parameters are not set correctly or the DC Injection / Position Lock Time at Stop (S1-05) is set to a value lower than the Brake Close Delay Time (S1-07). 

  1. Correct parameter settings so that S1-05 > S1-07.
  2. The deceleration distance (S5-11) is set to value lower than the minimum deceleration distance (U4-43).
  3. The stop distance (S5-12) is set to a value lower than the minimum stop distance (U4-44).
  4. Correct parameter settings so that S5-11 > U4-43.
  5. Correct parameter settings so that S5-12 > U4-44.
  6. Both S5-10 and S5-01 are enabled at the same time.
  7. Correct the setting in parameters S5-01 and S5-10.