Cause : Elevator Parameter Setting Fault comes when elevator parameters are not set correctly or the DC Injection / Position Lock Time at Stop (S1-05) is set to a value lower than the Brake Close Delay Time (S1-07).
- Correct parameter settings so that S1-05 > S1-07.
- The deceleration distance (S5-11) is set to value lower than the minimum deceleration distance (U4-43).
- The stop distance (S5-12) is set to a value lower than the minimum stop distance (U4-44).
- Correct parameter settings so that S5-11 > U4-43.
- Correct parameter settings so that S5-12 > U4-44.
- Both S5-10 and S5-01 are enabled at the same time.
- Correct the setting in parameters S5-01 and S5-10.