ov fault code in yaskawa Z1000 drive
Cause : Overvoltage comes when the voltage supplied to the drive has exceeded the acceptable limit or there are surge voltages in the input power supply.
Voltage in the DC bus has exceeded the overvoltage detection level.
• For 200 V class drives: approximately 410 V
• For 400 V class drives: approximately 820 V (740 V when E1-01 is less than 400)
  1. The deceleration time is too short and too much regenerative energy is flowing back into the drive.
    • Set L3-04 = 1 [Stall Prevention during Decel = General Purpose].
    • Connect a dynamic braking option to the drive.
    • Perform Deceleration Rate Tuning.
  2. The acceleration time is too short.
  3. Make sure that sudden drive acceleration does not cause the fault.
  4. The braking load is too large. Connect a dynamic braking option to the drive.
  5. There are surge voltages in the input power supply. Connect a DC link choke to the drive.
  6. The drive output cable or motor is shorted to ground (the current short to ground is charging the main circuit capacitor of the drive through the power supply).
    • Examine the motor main circuit cable, terminals, and motor terminal box, and then remove ground faults.
    • Re-energize the drive.
