SE4 fault code in yaskawa L1000A drive
Cause : Brake Feedback Error comes when the feedback contact on the brake is defective or the wiring is incorrect. The input terminal set for “Brake feedback” (H1-XX = 79) or “Brake feedback 2” (H1-XX = 5B) did not respond within the
SE4 error time set to S6-05 after an output terminal set for “Brake release” (H2-XX = 50) closed.
  1. Check the brake feedback contact and the wiring.
  2. The brake control circuit does not work properly.
  3. Ensure the motor brake operates properly with a brake control command from the drive.