Cause : DC Bus Undervoltage comes when there is a phase loss in the drive input power. Correct errors with the wiring for main circuit drive input power.
- Voltage in the DC bus fell below the undervoltage detection level (L2-05).
• For 200 V class drives: approximately 190 V.
• For 400 V class drives: approximately 440 when using input voltages 460 V or higher (350 V when E1-01 is less than 400, and 380 V when 400V ≤ E1-01 < 460 V ). - The fault is output only if L2-01 is set to 0 or 1 and the DC bus voltage has fallen below the level set to L2-05 for longer than the time set to L2-02.