ABB ACS550 Drive Fault Codes & Troubleshooting List (2026) – The ABB ACS550 is one of the most widely installed general-purpose drives in history. When the drive trips, the Assistant Control Panel displays a specific code starting with “F” (Fault) or a 4-digit number for Alarms (20xx).
This guide provides the most updated reference for maintaining this classic drive, helping you minimize downtime on aging equipment.
ACS550 Fault Codes Reference Table
Use the search bar below or browse the table to identify your specific error code.
| Code | Cause & Solution |
| F0001 OVERCURRENT | Cause: Output current has exceeded trip level. Solution: 1. Check motor load. 2. Check acceleration time (parameters 2202 ACCELER TIME 1 and 2205 ACCELER TIME 2). 3. Check motor and motor cable (including phasing). 4. Check ambient conditions. Load capacity decreases if installation site ambient temperature exceed 40 °C. |
| F0002 DC OVERVOLT | Cause: Excessive intermediate circuit DC voltage. DC overvoltage trip limit is 420 V for 200 V drives and 840 V for 400 V drives. Solutions: 1. Check that overvoltage controller is on (parameter 2005 OVERVOLT CTRL). 2. Check brake chopper and resistor (if used). DC overvoltage control must be deactivated when brake chopper and resistor are used. 3. Check deceleration time (parameters 2203 DECELER TIME 1 and 2206 DECELER TIME 2). 4. Check input power line for static or transient overvoltage. 5. Retrofit frequency converter with brake chopper and brake resistor. |
| F0003 DEV OVERTEMP | Cause: Drive IGBT temperature is excessive. Fault trip limit is 135 °C. Solution: 1. Check ambient conditions. 2. Check air flow and fan operation. 3. Check motor power against drive power. |
| F0004 SHORT CIRC | Cause: Short circuit in motor cable(s) or motor Solution: 1. Check motor and motor cable. |
| F0006 DC UNDERVOLTAGE | Cause: Intermediate circuit DC voltage is not sufficient due to missing input power line phase, blown fuse, rectifier bridge internal fault or too low input power. Solution: 1. Check that undervoltage controller is on (parameter 2006 UNDERVOLT CTRL). 2. Check input power supply and fuses. |
| F0007 AI1 LOSS | Cause: Analog input AI1 signal has fallen below limit defined by parameter 3021 AI1 FAULT LIMIT. Solution: 1. Check fault function parameter settings. 2. Check for proper analog control signal levels. 3. Check connections. |
| F0008 AI1 LOSS | Cause: Analog input AI2 signal has fallen below limit defined by parameter 3022 AI2 FAULT LIMIT. Solution: 1. Check fault function parameter settings. 2. Check for proper analog control signal levels. 3. Check connections. |
| F0009 MOT OVERTEMP | Cause: Motor temperature is too high (or appears to be too high) due to excessive load, insufficient motor power, inadequate cooling or incorrect start-up data. Solution: 1. Check motor ratings, load and cooling. 2. Check start-up data. 3. Check fault function parameter settings. 4. Let motor cool down. Ensure proper motor cooling: 5. Check cooling fan, clean cooling surfaces, etc. |
| F0010 PANEL LOSS | Cause: Control panel selected as active control location for drive has ceased communicating. Solution: 1. Check panel connection. 2. Check fault function parameters. 3. Check control panel connector. 4. Refit control panel in mounting platform. 5. If drive is in external control mode (REM) and is set to accept start/stop, direction commands or references through control panel: Check group 10 START/STOP/DIR and 11 REFERENCE SELECT settings. |
| F0011 ID RUN FAIL | Cause: Motor ID run is not completed successfully. Solution: 1. Check motor connection. 2. Check start-up data (group 99 START- UP DATA). 3. Check maximum speed (parameter 2002). It should be at least 80% of motor nominal speed (parameter 9908). 4. Ensure ID run has been performed |
| F0012 MOTOR STALL | Cause: Motor is operating in stall region due to, for example, excessive load or insufficient motor power. Solution: 1. Check motor load and drive ratings. 2. Check fault function parameter settings. |
| F0014 EXT FAULT 1 | Cause: External fault 1 Check external devices for faults. Solution: 1. Check fault function parameter setting. |
| F0015 EXT FAULT 2 | Cause: External fault 2 Solution: 1. Check external devices for faults. 2. Check fault function parameter setting. |
| F0016 EARTH FAULT | Cause: Drive has detected earth (ground) fault in motor or motor cable. Solution: 1. Check motor. 2. Check motor cable. 3. Motor cable length must not exceed maximum specifications. Note: Disabling earth fault (ground fault) may damage drive. |
| F0018 THERM FAIL | Cause: Drive internal fault. Thermistor used for drive internal temperature measurement is open or short-circuited. Solution: This hardware issue in drive need to repair or replace drive. |
| F0019 OPEX LINK | Cause: Internal fault. A communication-related problem has been detected on the fiber optic link between the control and OINT boards. Solution: Check connection. |
| F0020 OPEX PWR | Cause: Internal fault. Exceptionally low voltage detected on the OINT power supply. Solution: There is an hardware or software issue in drive, need to repaur or replace drive. |
| F0021 CURRENT MEAS | Cause: Drive internal fault. Current measurement is out of range. Solution: This hardware issue in drive need to repair or replace drive. |
| F0022 Supply PHASE LOSS | Cause: Intermediate circuit DC voltage is oscillating due to missing input power line phase or blown fuse. Fault trip occurs when DC voltage ripple exceeds 14% of nominal DC voltage. Solution: 1. Check input power line fuses. 2. Check for input power supply imbalance. 3. Check fault function parameter setting. |
| F0023 ENCODER ERROR | Cause: Communication fault between pulse encoder and pulse encoder interface module or between module and drive. Solution: 1. Check pulse encoder and its wiring, pulse encoder interface module and its wiring and parameter group 50 ENCODER settings. |
| F0024 OVERSPEED | Cause: Motor is turning faster than highest allowed speed due to incorrectly set minimum/maximum speed. Operating range limits are set by parameters 2007 MINIMUM FREQ and 2008 MAXIMUM FREQ. Solution: 1. Check minimum/maximum frequency settings. 2. Check adequacy of motor braking torque. |
F0026 DRIVE ID | Cause: Internal drive ID fault Solution: This hardware issue in drive need to repair or replace drive. |
| F0027 CONFIG FILE | Cause: Internal configuration file error. Solution: This hardware issue in drive need to repair or replace drive. |
| F0028 SERIAL 1 ERR | Cause: Fieldbus communication break. Solution: 1. Check status of fieldbus communication. 2. Check fault function parameter settings. 3. Check connections. 4. Check if master can communicate. |
| F0029 EFB CON FILE | Cause: Configuration file reading error. Solution: There is an hardware or software issue in drive, need to repaur or replace drive. |
| F0030 FORCE TRIP | Cause: Trip command received from fieldbus Solution: See appropriate communication module manual. |
| F0031 EFB 1 | Cause: Error from the embedded fieldbus (EFB) protocol application. The meaning is protocol dependent. Solution: Check communication parameter. |
| F0032 EFB 2 | Cause: Error from the embedded fieldbus (EFB) protocol application. The meaning is protocol dependent. Solution: Check communication parameter. |
| F0033 EFB 3 | Cause: Error from the embedded fieldbus (EFB) protocol application. The meaning is protocol dependent. Solution: Check communication parameter. |
| F0034 MOTOR PHASE | Cause: Motor circuit fault due to missing motor phase or motor thermistor relay (used in motor temperature measurement) fault. Solution: 1. Check motor and motor cable. 2. Check motor thermistor relay (if used). |
| F0035 OUTPUT WIRING | Cause: Incorrect input power and motor cable connection (that is input power cable is connected to drive motor connection). Fault can be erroneously declared if drive is faulty or input power is delta grounded system and motor cable capacitance is large. Solution: 1. Check input power connections. 2. Check input & output connection. |
| F0036 INCOMPATIBLE SW | Cause: Loaded software is not compatible. Solution: There is an hardware or software issue in drive, need to repaur or replace drive. |
| F0037 CB OVERTEMP | Cause: Drive control board overheated. Fault given when measured temperature of the control board. Parameter 3024 CB TEMP FAULT is set to enable with fault. Solution: 1. Check for excessive ambient temperature. 2. Check for fan failure. 3. Check for obstructions in air flow. 4. Check the dimensioning and cooling of cabinet. |
| F0038 USER LOAD CURVE | Cause: Condition defined by 3701 USER LOAD C MODE has been valid longer than the time set by 3703 USER LOAD C TIME. Solution: See parameter group 37 USER LOAD CURVE. |
| F0101… F0199 SYSTEM ERROR | Cause: Error internal to the drive. Solution: There is an hardware or software issue in drive, need to repaur or replace drive. |
| F0201… F0299 SYSTEM ERROR | Cause: Error internal to the drive. Solution: There is an hardware or software issue in drive, need to repaur or replace drive. |
| F1000 PAR HZRPM | Cause: Incorrect speed/frequency limit parameter setting Solution: 1. Parameter values are inconsistent. Check for any of the following: • 2001 MINIMUM SPEED > 2002 MAXIMUM SPEED . • 2007 MINIMUM FREQ > 2008 MAXIMUM FREQ. • 2001 MINIMUM SPEED / 9908 MOTOR NOM SPEED is outside proper range (> 50). • 2002 MAXIMUM SPEED / 9908 MOTOR NOM SPEED is outside proper range (> 50). • 2007 MINIMUM FREQ / 9907 MOTOR NOM FREQ is outside proper range (> 50). • 2008 MAXIMUM FREQ / 9907 MOTOR NOM FREQ is outside proper range (> 50). |
F1001 PAR PFC REF NEG | Cause: Incorrect PFC parameters. Solution: 1. Check parameter group 81 PFC CONTROL settings. 2. Check that following applies: • 2007 MINIMUM FREQ > 0 when 8123 is ACTIVE or SPFC ACTIVE. |
| F1003 PAR AI SCALE | Cause: Incorrect analog input AI signal scaling. Solution: 1. Check parameter group 13 ANALOG INPUTS settings. 2. Check that following applies: • 1301 MINIMUM AI1 < 1302 MAXIMUM AI1 • 1304 MINIMUM AI2 < 1305 MAXIMUM AI2. |
| F1004 PAR AO SCALE | Cause: Incorrect analog output AO signal scaling. Solution: 1. Check parameter group 15 ANALOG OUTPUTS settings. 2. Check that following applies: • 1504 MINIMUM AO1 < 1505 MAXIMUM AO1. |
| F1005 PAR PCU 2 | Cause: Incorrect motor nominal power setting. Solution: Check parameter 9909 MOTOR NOM POWER setting. Following must apply: • 1.1 < (9906 MOTOR NOM CURR · 9905 MOTOR NOM VOLT · 1.73 / PN ) < 3.0 Where PN = 1000 · 9909 MOTOR NOM POWER (if units are in kW) or PN = 746 · 9909 MOTOR NOM POWER (if units are in hp). |
| F1006 PAR EXT RO | Cause: Incorrect extension relay output parameters Solution: 1. Parameter values are inconsistent. Check for the following: • Extension relay module not connected and • 1410…1412 RELAY OUTPUTS 4…6 have non-zero values. |
| F1007 PAR FIELDBUS MISSING | Cause: Fieldbus control has not been activated. Solution: 1. Check fieldbus parameter settings. |
| F1008 PAR PFC MODE | Cause: Parameter values are inconsistent – 9904 MOTOR CTRL MODE must be = 3 ( SCALAR :FREQ), when 8123 PFC ENABLE is activated. |
| F1009 PAR PCU 1 | Cause: Incorrect motor nominal speed/frequency setting. Solution: 1. Check parameter settings. 2. Following must apply for induction motor: • 1 < (60 · 9907 MOTOR NOM FREQ / 9908 MOTOR NOM SPEED) < 16 • 0.8 < 9908 MOTOR NOM SPEED / (60 · 9907 MOTOR NOM FREQ / 9913 MOTOR POLE PAIRS) < 0.992 3. Following must apply for permanent magnet synchronous motor: • 9908 MOTOR NOM SPEED / (60 · 9907 MOTOR NOM FREQ / 9913 MOTOR POLE PAIRS) = 1.0 |
| F1012 PAR PFC IO 1 | Cause: I/O configuration for PFC not complete. Solution: 1. Check parameter settings. Following must apply: • There are enough relays parameterized for PFC. • No conflict exists between parameter group 14 RELAY OUTPUTS, parameter 8117 NR OF AUX MOT and parameter 8118 AUTOCHNG INTERV. |
| F1013 PAR PFC IO 2 | Cause: I/O configuration for PFC not complete. Solution: 1.Check parameter settings. Following must apply: • The actual number of PFC motors (parameter 8127 MOTORS) matches the PFC motors in parameter group 14 RELAY OUTPUTS and parameter 8118 AUTOCHNG INTERV. |
| F1014 PAR PFC IO 3 | Cause: I/O configuration for PFC not complete. The drive is unable to allocate a digital input (interlock) for each PFC motor. Solution: See parameters 8120 INTERLOCKS and 8127 MOTORS. |
| F1016 PAR USER LOAD C | Cause: Incorrect user load curve parameter setting. Solution: 1. Check parameter settings. Following must apply: • 3704 LOAD FREQ 1 < 3707 LOAD FREQ 2 < 3710 LOAD FREQ 3 < 3713 LOAD FREQ 4 < 3716 LOAD FREQ 5 • 3705 LOAD TORQ LOW 1 < 3706 LOAD TORQ HIGH 1 • 3708 LOAD TORQ LOW 2 < 3709 LOAD TORQ HIGH 2 • 3711 LOAD TORQ LOW 3 < 3712 LOAD TORQ HIGH 3 • 3714 LOAD TORQ LOW 4 < 3715 LOAD TORQ HIGH 4 • 3717 LOAD TORQ LOW 5 < 3718 LOAD TORQ HIGH 5. |
| A2001 OVERCURRENT | Cause: Output current limit controller is active. Solution: 1. Check motor load. 2. Check acceleration time (parameters 2202 ACCELER TIME 1 and 2205 ACCELER TIME 2). 3. Check motor and motor cable (including phasing). 4. Check ambient conditions. |
| A2002 OVERVOLTAGE | Cause: DC overvoltage controller is active. Solution: 1. Check deceleration time (parameters 2203 DECELER TIME 1 and 2206 DECELER TIME 2). 2. Check input power line for static or transient overvoltage. |
| A2003 UNDERVOLTAGE | Cause: DC undervoltage controller is active. Solution: Check input power supply. |
| A2004 DIRLOCK | Cause: Change of direction is not allowed. Solution: Check parameter 1003 DIRECTION settings. |
| A2005 IO COMM | Cause: Fieldbus communication break. Solution: 1. Check status of fieldbus communication. 2. Check fault function parameter settings. 3. Check connections. 4. Check if master can communicate. |
| A2006 AI1 LOSS | Cause: Analog input AI1 signal has fallen below limit defined by parameter 3021 AI1 FAULT LIMIT. Solution: 1. Check fault function parameter settings. 2. Check for proper analog control signal levels. 3. Check connections. |
| A2007 AI2 LOSS | Cause: Analog input AI2 signal has fallen below limit defined by parameter 3022 AI1 FAULT LIMIT. Solution: 1. Check fault function parameter settings. 2. Check for proper analog control signal levels. 3. Check connections. |
| A2008 PANEL LOSS | Cause: Control panel selected as active control location for drive has ceased communicating. Solution: 1. Check panel connection. 2. Check fault function parameters. 3. Check control panel connector. 4. Refit control panel in mounting platform. 5. If drive is in external control mode (REM) and is set to accept start/stop, direction commands or references through control panel: Check group 10 START/STOP/DIR and 11 REFERENCE SELECT settings. |
| A2009 DEVICE OVERTEMP | Cause: Drive IGBT temperature is excessive. Alarm limit is 120 °C. Solution: 1. Check ambient conditions. 2. Check air flow and fan operation. 3. Check motor power against drive power. |
| A2010 MOTOR TEMP | Cause: Motor temperature is too high (or appears to be too high) due to excessive load, insufficient motor power, inadequate cooling or incorrect start-up data. Solution: 1. Check motor ratings, load and cooling. 2. Check start-up data. 3. Check fault function parameter settings. 4. Let motor cool down. 5. Ensure proper motor cooling: Check cooling fan, clean cooling surfaces, etc. |
| A2012 MOTOR STALL | Cause: Motor is operating in stall region due to, for example, excessive load or insufficient motor power. Solution: 1. Check motor load and drive ratings. 2. Check fault function parameter settings. |
| A2013 AUTORESET | Cause: Automatic reset alarm. Solution: Check parameter group 31 AUTOMATIC RESET settings. |
| A2014 AUTOCHANGE | Cause: PFC Autochange function is active. Solution: See parameter group 81 PFC CONTROL. |
| A2015 PFC I LOCK | Cause: PFC Interlocks are active. Solution: 1. Drive cannot start • any motor (when Autochange is used) • the speed regulated motor (when Autochange is not used). |
| A2018 PID SLEEP | Cause: Sleep function has entered the sleeping mode. Solution: See parameter groups 40 PROCESS PID SET 1… 41 PROCESS PID SET 2. |
| A2019 ID RUN | Cause: Motor Identification run is on. Solution: This alarm belongs to normal start-up procedure. Wait until drive indicates that motor identification is completed. |
| A2021 START ENABLE 1 MISSING | Cause: No Start enable 1 signal received. Solution: 1. Check parameter 1608 START ENABLE 1 settings. 2. Check digital input connections. 3. Check fieldbus communication settings. |
| A2022 START ENABLE 2 MISSING | Cause: No Start enable 2 signal received. Solution: 1. Check parameter 1609 START ENABLE 2 settings. 2. Check digital input connections. 3. Check fieldbus communication settings. |
| A2023 EMERGENCY STOP | Cause: Drive has received emergency stop command and ramps to stop according to ramp time defined by parameter 2208 EMERG DEC TIME. Solution: 1. Check that it is safe to continue operation. 2. Return emergency stop push button to normal position. |
| A2024 ENCODER ERROR | Cause: Communication fault between pulse encoder and pulse encoder interface module or between module and drive. Solution: 1. The drive is not detecting a valid encoder signal. Check for and correct: • Encoder presence and proper connection (reverse wired, loose connection or short circuit). • Voltage logic levels are outside of the specified range. • A working and properly connected Pulse Encoder Interface Module, OTAC-01. • Wrong value entered in parameter 5001 PULSE NR. A wrong value will only be detected if the error is such that the calculated slip is greater than 4 times the rated slip of the motor. • Encoder is not being used, but parameter 5002 ENCODER ENABLE = 1 (ENABLE). |
| A2025 FIRST START | Cause: Motor identification magnetization is on. This alarm belongs to normal start-up procedure. Solution: Wait until drive indicates that motor identification is completed. |
| A2027 USER LOAD CURVE | Cause: Condition defined by 3701 USER LOAD C MODE has been valid longer than half of the time set by 3703 USER LOAD C TIME. Solution: See parameter group 37 USER LOAD CURVE. |
| A2028 START DELAY | Cause: Start delay in progress Solution: See parameter 2113 START DELAY. |
| A5001 | Cause: Drive is not responding. Solution: Check panel connection. |
| A5002 | Cause: Incompatible communication profile. Solution: There is an hardware or software issue in drive, need to repaur or replace drive. |
| A5010 | Cause: Corrupted panel parameter backup file Solution: 1. Retry parameter upload. 2. Retry parameter download. |
| A5011 | Cause: Drive is controlled from another source. Solution: Change drive control to the local control mode. |
| A5012 | Cause: Direction of rotation is locked. Solution: Enable change of direction. See parameter 1003 DIRECTION. |
| A5013 | Cause: Panel control is disabled because start inhibit is active. Solution: 1. Start from the panel is not possible. Reset the emergency stop command or remove the 3-wire stop command before starting from the panel. 2. Check parameters 1001 EXT1 COMMANDS, 1002 EXT2 COMMANDS and 2109 EMERG STOP SEL. |
| A5014 | Cause: Panel control is disabled because of drive fault. Solution: Reset drive fault and retry. |
| A5015 | Cause: Panel control is disabled because the local control mode lock is active. Solution: Deactivate the local control mode lock and retry. See parameter 1606 LOCAL LOCK. |
| A5018 | Cause: Parameter default value is not found. Solution: There is an hardware or software issue in drive, need to repaur or replace drive. |
| A5019 | Cause: Writing non-zero parameter value is prohibited. Solution: Only parameter reset is allowed. |
| A5020 | Cause: Parameter or parameter group does not exist or parameter value is inconsistent. Solution: There is an hardware or software issue in drive, need to repaur or replace drive. |
| A5021 | Cause: Parameter or parameter group is hidden. Solution: There is an hardware or software issue in drive, need to repaur or replace drive. |
| A5022 | Cause: Parameter is write protected. Solution: Parameter value is read-only and cannot be changed. |
| A5023 | Cause: Parameter change is not allowed, when drive is running. Solution: Stop drive and change parameter value. |
| A5024 | Cause: Drive is executing task. Solution: Wait until task is completed. |
| A5025 | Cause: Software is being uploaded or downloaded. Solution: Wait until upload/download is complete. |
| A5026 | Cause: Value is at or below minimum limit. |
| A5027 | Cause: Value is at or above maximum limit. |
| A5028 | Cause: Invalid value |
| A5029 | Cause: Memory is not ready. Solution: Retry. |
| A5030 | Cause: Invalid request |
| A5031 | Cause: Drive is not ready for operation, for example, due to low DC voltage. Solution: Check input power supply. |
| A5032 | Cause: Parameter error. |
| A5040 | Cause: Parameter download error. Selected parameter set is not in current parameter backup file. Solution: Perform upload function before download. |
| A5041 | Cause: Parameter backup file does not fit into memory. Solution: There is an hardware or software issue in drive, need to repaur or replace drive. |
| A5042 | Cause: Parameter download error. Selected parameter set is not in current parameter backup file. Solution: Perform upload function before download. |
| A5043 | Cause: No start inhibit. |
| A5044 | Cause: Parameter backup file restoring error. Solution: 1. Check that file is compatible with drive. |
| A5050 | Cause: Parameter upload aborted. Solution: 1. Retry parameter upload. |
| A5051 | Cause: File error. Solution: There is an hardware or software issue in drive, need to repaur or replace drive. |
| A5052 | Cause: Parameter upload has failed. Solution: Retry parameter upload. |
| A5060 | Cause: Parameter download aborted. Solution: 1. Retry parameter download. |
| A5062 | Cause: Parameter download has failed. Solution: Retry parameter download. |
| A5070 | Cause: Panel backup memory write error. Solution: There is an hardware or software issue in drive, need to repaur or replace drive. |
| A5071 | Cause: Panel backup memory read error. Solution: There is an hardware or software issue in drive, need to repaur or replace drive. |
A5080 | Cause: Operation is not allowed because the drive is not in the local control mode. Solution: Switch to the local control mode. |
| A5081 | Cause: Operation is not allowed because of active fault. Solution: Check cause of fault and reset fault. |
| A5083 | Cause: Operation is not allowed because parameter lock is on. Solution: Check parameter 1602 PARAMETER LOCK setting. |
| A5084 | Cause: Operation is not allowed because drive is performing a task. Solution: Wait until task is completed and retry. |
| A5085 | Cause: Parameter download from source to destination drive has failed. Solution: 1. Check that source and destination drive types are same. See the type designation label of the drive. |
| A5086 | Cause: Parameter download from source to destination drive has failed. Solution: 1. Check that source and destination drive type designations are the same. 2. See type designation labels of the drives. |
| A5087 | Cause: Parameter download from source to destination drive has failed because parameter sets are incompatible. Solution: 1. Check that source and destination drive information are same. See parameters in group 33 INFORMATION. |
| A5088 | Cause: Operation has failed because of drive memory error. Solution: There is an hardware or software issue in drive, need to repaur or replace drive. |
| A5089 | Cause: Download has failed because of CRC error. Solution: There is an hardware or software issue in drive, need to repaur or replace drive. |
| A5090 | Cause: Download has failed because of data processing error. Solution: There is an hardware or software issue in drive, need to repaur or replace drive. |
| A5091 | Cause: Operation has failed because of parameter error. Solution: There is an hardware or software issue in drive, need to repaur or replace drive. |
| A5092 | Cause: Parameter download from source to destination drive has failed because parameter sets are incompatible. Solution: 1. Check that source and destination drive information are same. See parameters in group 33 INFORMATION. |
How to Read ACS550 Faults via Panel & Software
The ACS550 relies on the DriveWindow Light platform. Here is how to access diagnostics in 2026:
- Assistant Control Panel (Keypad): The ACS550 assistant panel features a Real-Time Clock.
- Maintenance Tip: If your fault logs show incorrect dates (e.g., year 2002), the CR2032 battery inside the control panel likely needs replacing. Accurate timestamps are critical for troubleshooting.
- Parameter Group 04 (Fault History):
- 0401: Last Fault Code.
- 0402/0403: Fault Time (Day/Time).
- 0412: Previous Fault Code.
- 0413: Fault Type (identifies if it was an alarm or trip).
- DriveWindow Light (PC Tool): Connect via the RS-232 port (often requires a USB-to-Serial adapter). This software allows you to view the “Fault Logger” and back up parameters (.dwp files) before attempting a reset or board replacement.
Q: What is the difference between an Alarm and a Fault on the ACS550?
A:
- Alarm (Codes 2001–2028): The drive detects a non-critical issue (e.g., Alarm 2010 “Motor Overterm”) but continues running. The green LED on the panel will flash.
- Fault (Codes F0001–F0045): The drive stops modulation immediately to protect the hardware. The red LED turns solid.
Q: How do I reset an ABB ACS550 fault?
A:
- Press the RESET key on the control panel.
- Toggle the defined Digital Input (Parameter 1604, usually set to DI4).
- Power cycle the unit (wait 5 minutes for the DC bus to discharge).
Q: My ACS550 displays “F0001 Overcurrent” immediately upon start. What should I check?
A: This is the most common fault. Check the motor insulation (megger test), ensure the acceleration ramp time (Param 2202) isn’t too short, and verify the motor nameplate data matches Group 99 parameters.