Digitax HD M754 MCi Drive Fault Codes (2026) – Troubleshooting guide for the Nidec Digitax HD M754. Learn to interpret mnemonic trip codes, troubleshoot integrated MCi controller errors, and debug CODESYS user trips.
The Nidec Control Techniques Digitax HD M754 is a specialized high-performance servo drive that features a powerful **integrated MCi motion controller**. Unlike standard drives, the M754 acts as a dual-processor system: one processor handles the motor control and power stage, while the second (the MCi) runs complex motion logic and decentralized programs. When the drive identifies an error, it stops the motor and displays a mnemonic trip code—such as OI.AC (Overcurrent) or User Trip.
This 2026 guide provides a diagnostic framework specifically for the M754, helping you differentiate between base drive hardware trips and logical errors originating from the internal motion controller.
Digitax HD M754 Fault Codes Reference Table
Below is the complete reference list of faults for the Digitax HD M754. Because this drive runs independent user programs, pay close attention to trips labeled as “User,” as these are defined by the internal CODESYS application.
| Fault Code and Meaning | Cause and Remedy | ||||||||||||||||
| 217 App Menu Changed | Cause: The customization table for an application menu has changed. The menu that has changed can be identified by the sub-trip number:
| 11 Autotune 1 | Cause: Position feedback did not change or required speed could not be reached during autotune.
| 12 Autotune 2 | Cause: Position feedback direction incorrect.
| 13 Autotune 3 | Cause: Measured inertia exceeded parameter range or commutation signals changed in wrong direction.
| 14 Autotune 4 | Cause: Drive encoder U commutation signal fail. The U commutation signal did not change during a rotating autotune. Remedy:
| 15 Autotune 5 | Cause: Drive encoder V commutation signal fail. The V commutation signal did not change during a rotating autotune. Remedy:
| 16 Autotune 6 | Cause: Drive encoder W commutation signal fail. The W commutation signal did not change during a rotating autotune. Remedy:
| 17 Autotune 7 | Cause: Motor number of poles / position feedback resolution set incorrectly. Remedy:
| 18 Autotune Stopped | Cause: Autotune test stopped before completion. Either drive enable or drive run were removed. Remedy:
| 19 Brake R Too Hot | Cause: Braking resistor overload timed out (I²t). Braking Resistor Thermal Accumulator (10.039) reached 100%. Remedy:
| 99 CAM | Cause: Advanced motion controller CAM failure.
| 185 Card Access | Cause: SD Card Write fail. Unable to access SD Card or data transfer corrupted. Remedy:
| 177 Card Boot | Cause: The Menu 0 parameter modification cannot be saved to the SD Card. Boot file not created to take new parameter value. Remedy:
| 178 Card Busy | Cause: SD Card cannot be accessed as it is being accessed by an option module. Remedy:
| 188 Card Compare | Cause: SD Card file/data is different to the one in the drive. Remedy:
| 179 Card Data Exists | Cause: SD Card data location already contains data. Remedy:
| 187 Card Drive Mode | Cause: SD Card parameter set not compatible with current drive mode. Remedy:
| 182 Card Error | Cause: SD Card data structure error.
| 184 Card Full | Cause: SD Card full. Not enough space left on the card. Remedy:
| 183 Card No Data | Cause: SD Card data not found. Attempted to access non-existent file or block. Remedy:
| 180 Card Option | Cause: SD Card trip; option modules installed are different between source drive and destination drive. Remedy:
| 175 Card Product | Cause: SD Card data blocks are not compatible with the drive derivative.
| 186 Card Rating | Cause: The voltage and / or current rating of the source and destination drives are different. Remedy:
| 181 Card Read Only | Cause: SD Card has the Read Only bit set. Remedy:
| 174 Card Slot | Cause: Option module application program transfer has failed. Remedy:
| 35 Control Word | Cause: Trip initiated from the Control Word (06.042) by setting bit 12. Remedy:
| 225 Current Offset | Cause: Current feedback offset error. Offset too large to be trimmed.
| 97 Data Changing | Cause: Drive parameters are being changed by user action or file system write while drive is enabled. Remedy:
| 247 Derivative ID | Cause: Derivative identification error.
| 248 Derivative Image | Cause: Derivative Image error.
| 199 Destination | Cause: Two or more parameters are writing to the same destination parameter. Remedy:
| 224 Drive Size | Cause: Power stage recognition: Unrecognized drive size. Control PCB has not recognized power circuit size. Remedy:
| 31 EEPROM Fail | Cause: Default parameters have been loaded. EEPROM failure or corruption.
| 189 Encoder 1 | Cause: Drive position feedback interface power supply overload (Terminals 13 & 14). Remedy:
| 190 Encoder 2 | Cause: Drive encoder (Feedback) wire break.
| 191 Encoder 3 | Cause: Phase offset incorrect while running. The drive has detected an incorrect UVW phase angle while running (RFC-S mode only) or SINCOS phase error. Remedy:
| 192 Encoder 4 | Cause: Feedback device comms failure. Encoder communications has timed out or the communications position message transfer time is too long. Can also be caused by a wire break. Remedy:
| 193 Encoder 5 | Cause: Checksum or CRC error. There is a checksum or CRC error, or the SSI encoder is not ready. Can also indicate a wire break to a communications based encoder. Remedy:
| 194 Encoder 6 | Cause: Encoder has indicated an error. The encoder has indicated an error or the power supply has failed to an SSI encoder. Remedy:
| 195 Encoder 7 | Cause: Set-up parameters for position feedback device have changed. Remedy:
| 196 Encoder 8 | Cause: Position feedback interface has timed out. Interface communications time exceeds 250 μs. Remedy:
| 197 Encoder 9 | Cause: Position feedback is selected from an option module slot which does not have a feedback option module installed. Remedy:
| 162 Encoder 12 | Cause: Encoder could not be identified during auto-configuration. The drive is communicating with the encoder but the encoder type is not recognized. Remedy:
| 163 Encoder 13 | Cause: Data read from the encoder is out of range during auto-configuration.
| 6 External Trip | Cause: An External Trip has been initiated. This can be caused by digital input states (Safe Torque Off) or by writing a value of 6 in Pr 10.038. Remedy:
| HF01 CPU address error | Cause: Data processing error: CPU address error. Control PCB failure. Remedy:
| HF02 DMAC address error | Cause: Data processing error: DMAC address error. Control PCB failure. Remedy:
| HF03 Illegal instruction | Cause: Data processing error: Illegal instruction. Control PCB failure. Remedy:
| HF04 Illegal slot instruction | Cause: Data processing error: Illegal slot instruction. Control PCB failure. Remedy:
| HF05 Undefined exception | Cause: Data processing error: Undefined exception error. Control PCB failure. Remedy:
| HF06 Reserved exception | Cause: Data processing error: Reserved exception error. Control PCB failure. Remedy:
| HF07 Watchdog failure | Cause: Data processing error: Watchdog failure. Control PCB failure. Remedy:
| HF08 CPU Interrupt crash | Cause: Data processing error: CPU interrupt crash. Control PCB failure. Remedy:
| HF09 Free store overflow | Cause: Data processing error: Free store overflow. Control PCB failure. Remedy:
| HF10 Parameter routing system error | Cause: Data processing error: Parameter routing system error. Control PCB failure. Remedy:
| HF11 Access to EEPROM failed | Cause: Data processing error: Access to the drive EEPROM has failed. Control PCB failure. Remedy:
| HF12 Main program stack overflow | Cause: Data processing error: Main program stack overflow. Remedy:
| HF13 Firmware incompatible with hardware | Cause: Data processing error: Drive firmware is not compatible with the hardware. Remedy:
| HF14 CPU register bank error | Cause: Data processing error: CPU register bank error. Control PCB failure. Remedy:
| HF15 CPU divide error | Cause: Data processing error: CPU divide error. Control PCB failure. Remedy:
| HF16 RTOS error | Cause: Data processing error: RTOS error. Control PCB failure. Remedy:
| HF17 Clock supplied to control board out of specification | Cause: Data processing error: Clock supplied to the control board logic is out of specification. Control PCB failure. Remedy:
| HF18 Internal flash memory has failed | Cause: Data processing error: Internal flash memory failed when writing option module parameter data. Remedy:
| HF19 CRC check on the firmware has failed | Cause: Data processing error: CRC check on the drive firmware has failed. Remedy:
| HF20 ASIC is not compatible with the hardware | Cause: Data processing error: The ASIC version is not compatible with the drive firmware. Remedy:
| HF23 to HF25 Hardware fault | Cause: Hardware fault. Remedy:
| 8 Inductance | Cause: Inductance measurement out of range or motor saturation not detected. Occurs in RFC-S mode when motor inductances are not suitable or saturation cannot be measured.
| 93 Inductor Too Hot | Cause: The regen inductor has overloaded. Thermal overload based on Rated Current and Inductor Thermal Time Constant. Trip occurs when temp reaches 100%. Remedy:
| 26 I/O Overload | Cause: Digital output overload. Total current drawn from 24 V user supply or from the digital output has exceeded the limit (100 mA). Remedy:
| 160 Island | Cause: Island condition detected in regen mode. AC mains is no longer present and the inverter would be an ‘islanded’ power supply. Remedy:
| 34 Keypad Mode | Cause: Keypad has been removed when the drive is receiving the speed reference from the keypad. Remedy:
| 39 Line Sync | Cause: Synchronization to the power supply has been lost in Regen mode. Remedy:
| 20 Motor Too Hot | Cause: Output current overload timed out (I2t). Motor thermal overload based on Rated Current and Motor Thermal Time Constant. Remedy:
| 176 Name Plate | Cause: Electronic nameplate transfer has failed. Remedy:
| 101 OHt Brake | Cause: Braking IGBT over-temperature. Based on software thermal model. Remedy:
| 23 OHt Control (Control stage over temperature) | Cause: A control stage over-temperature has been detected. From the sub-trip ‘xxyzz’, the Thermistor location is identified by ‘zz’. Remedy:
| 27 OHt dc bus (DC bus over temperature) | Cause: A DC bus component over temperature based on a software thermal model. The drive includes a thermal protection system to protect the DC bus components within the drive. Remedy:
| 21 OHt Inverter (Inverter over temperature based on thermal model) | Cause: An IGBT junction over-temperature has been detected based on a software thermal model. Remedy:
| 22 OHt Power (Power stage over temperature) | Cause: A power stage over-temperature has been detected. From the sub-trip ‘xxyzz’, the Thermistor location is identified by ‘zz’. Remedy:
| 3 OI ac (Instantaneous output over current detected) | Cause: The instantaneous drive output current has exceeded VM_DRIVE_CURRENT[MAX]. This trip cannot be reset until 10 s after the trip was initiated. Remedy:
| 4 OI Brake (Braking IGBT over current detected) | Cause: Over current has been detected in braking IGBT or braking IGBT protection has been activated. Short circuit protection for the braking IGBT activated. Remedy:
| 109 OI dc (Power module over current detected from IGBT on state voltage monitoring) | Cause: The short circuit protection for the drive output stage has been activated. The table shows where the trip has been detected. Remedy:
| 92 OI Snubber (Snubber over-current detected) | Cause: An over-current condition has been detected in the rectifier snubber circuit. Remedy:
| 215 Option Disable | Cause: The option module did not acknowledge to the drive that communications with the drive has been stopped during the drive mode changeover within the allocated time. Remedy:
| 98 Out Phase Loss (Output phase loss detected) | Cause: Phase loss has been detected at the drive output. Remedy:
| 7 Over Speed (Motor speed has exceeded the over speed threshold) | Cause: In open loop mode, Output Frequency exceeds the threshold. In RFC mode, Speed Feedback exceeds Over Speed Threshold. Remedy:
| 2 Over Volts (DC bus voltage has exceeded the peak level or maximum continuous level) | Cause: The DC bus voltage has exceeded the VM_DC_VOLTAGE[MAX] or VM_DC_VOLTAGE_SET[MAX] for 15 s. Remedy:
| 32 Phase Loss (Supply phase loss) | Cause: Input phase loss or large supply imbalance detected. Can be detected via thyristor base charge system or DC bus voltage ripple. Remedy:
| 198 Phasing Error (RFC-S mode phasing failure due to incorrect phase angle) | Cause: The phase offset angle in Pr 03.025 is incorrect if position feedback is being used and the drive is unable to control the motor correctly. Remedy:
| 90 Power Comms (Communication lost / errors detected between power, control and rectifier modules) | Cause: A communications problem within the power system of the drive. The reason for the trip can be identified by the sub-trip number. Remedy:
| 220 Power Data (Power system configuration data error) | Cause: There is an error in the configuration data stored in the power system. Remedy:
| 37 Power Down Save (Power down save error) | Cause: An error has been detected in the power down save parameters saved in non-volatile memory. Remedy:
| 5 PSU (Internal power supply fault) | Cause: One or more internal power supply rails are outside limits or overloaded. Remedy:
| 9 PSU 24V (24V internal power supply overload) | Cause: The total user load of the drive and option modules has exceeded the internal 24 V power supply limit. Remedy:
| 33 Resistance (Measured resistance has exceeded the parameter range) | Cause: The value being used for motor stator resistance is too high or an attempt to do a test involving measuring motor stator resistance has failed. Remedy:
| 254 Slot3 Different (Ethernet interface in slot 3 has changed) | Cause: The Ethernet interface in slot 3 has changed / not found. Remedy:
| 252 Slot3 Error | Cause: The Ethernet interface in slot 3 on the drive has detected an error. The reason for the trip can be identified by the sub-trip number (see manual for full list 100-228). Remedy:
| 250 Slot3 HF (Hardware Fault) | Cause: The Ethernet interface in slot 3 cannot operate. Common sub-trips:
| 253 Slot3 Not Fitted | Cause: The Ethernet interface in slot 3 on the drive has been removed since the last power-up. Remedy:
| 251 Slot3 Watchdog | Cause: The Ethernet interface installed in slot 3 has started the option watchdog function and then failed to service the watchdog correctly. Remedy:
| 216 Slot App Menu | Cause: More than one option slot has requested to customize the application menus 18, 19 and 20. The sub-trip number indicates which option slot has been allowed to customize the menus. Remedy:
| 204, 209, 214 SlotX Different | Cause: The option module in option slot X is a different type to that installed when parameters were last saved. Sub-trip identifies the original module. Remedy:
| 202, 207, 212 SlotX Error | Cause: The option module in option slot X on the drive has detected an error. The reason can be identified by the sub-trip number. Remedy:
| 200, 205, 210 SlotX HF (Hardware Fault) | Cause: The option module in option slot X cannot operate. Common sub-trips:
| 203, 208, 213 SlotX Not Fitted | Cause: The option module in option slot X on the drive has been removed since the last power up. Remedy:
| 201, 206, 211 SlotX Watchdog | Cause: The option module installed in Slot X has started the option watchdog function and then failed to service the watchdog correctly. Remedy:
| 226 Soft Start | Cause: The soft start relay in the drive failed to close or the soft start monitoring circuit has failed. Remedy:
| 221 Stored HF | Cause: A hardware trip (HF01 – HF20) has occurred and the drive has been power cycled. The sub-trip number identifies the HF trip (e.g. stored HF.17). Remedy:
| 227 Sub-array RAM | Cause: RAM allocation error. An option module, derivative image, or user program has requested more parameter RAM than allowed. Sub-trip = (parameter size) + (parameter type) + sub-array number. Remedy:
| 218 Temp Feedback | Cause: An internal thermistor has failed. Location identified by sub-trip (xx y zz).
| 10 Th Brake Res | Cause: Brake resistor over temperature. Hardware based braking resistor thermal monitoring is connected and the resistor overheats. Remedy:
| 25 Th Short Circuit | Cause: Motor thermistor short circuit. The motor thermistor is short circuit or low impedance (< 50 Ω). Sub-trip 4: Position feedback interface. Remedy:
| 24 Thermistor | Cause: Motor thermistor over-temperature. The motor thermistor connected to the drive has indicated a motor over temperature. Remedy:
| 110 Undefined | Cause: The power system has generated but did not identify the trip from the power system. The cause is unknown. Remedy:
| 249 User Program | Cause: On board user program error. An error has been detected in the onboard user program image. Common Sub-trips:
| 96 User Prog Trip | Cause: Trip generated by an onboard user program using a function call which defines the sub-trip number. Remedy:
| 36 User Save | Cause: User Save error / not completed. Error detected in user save parameters or power removed during save. Remedy:
| 40-89 112-159 User Trip | Cause: User generated trip. These trips are not generated by the drive and are to be used by the user to trip the drive through an application program. Remedy:
| 169 Voltage Range | Cause: Supply voltage out of range detected in Regen mode. Supply is outside the range defined by Regen Minimum/Maximum Voltage settings. Remedy:
| 30 Watchdog | Cause: Control word watchdog has timed out. The control word has been enabled and has timed out. Remedy:
| 32 Phase Loss | Cause: The drive has detected an input phase loss or large supply imbalance. Phase loss can be detected directly from the supply where the drive has a thyristor base charge system (Frame size 8 and above) or by monitoring the ripple in the DC bus voltage. Remedy:
| 198 Phasing Error | Cause: RFC-S mode phasing failure due to incorrect phase angle. The phase offset angle in Pr 03.025 (or Pr 21.020) is incorrect if position feedback is being used and the drive is unable to control the motor correctly. Remedy:
| 90 Power Comms | Cause: Communication has been lost or errors detected between power, control, and rectifier modules. A Power Comms trip indicates a communications problem within the power system of the drive. Remedy:
| 220 Power Data | Cause: Power system configuration data error. The Power Data trip indicates that there is an error in the configuration data stored in the power system. This can occur if the control board data table does not match the power board hardware identifier, or if there are CRC errors. Remedy:
| 37 Power Down Save | Cause: Power down save error. The trip indicates that an error has been detected in the power down save parameters saved in non-volatile memory. Remedy:
| 5 PSU | Cause: Internal power supply fault. One or more internal power supply rails are outside limits or overloaded. Remedy:
| 9 PSU 24V | Cause: 24V internal power supply overload. The total user load of the drive and option modules has exceeded the internal 24 V power supply limit. Remedy:
| 33 Resistance | Cause: Measured resistance has exceeded the parameter range. Either the value being used for motor stator resistance is too high, or an attempt to measure it failed. Remedy:
| 254 Slot3 Different | Cause: Ethernet interface in slot 3 has changed. The interface was changed or not found. Remedy:
| 252 Slot3 Error | Cause: Ethernet interface in slot 3 has detected a fault. Reasons include Link Loss, E/IP Timeout, Modbus Timeout, Watchdog errors, Firmware invalid, etc. Remedy:
| 250 Slot3 HF | Cause: Ethernet interface in slot 3 hardware fault. The interface cannot operate. Remedy:
| 253 Slot3 Not Fitted | Cause: Ethernet interface in slot 3 has been removed since the last power-up. Remedy:
| 251 Slot3 Watchdog | Cause: Ethernet interface watchdog service error. The interface started the watchdog function and then failed to service it correctly. Remedy:
| 216 Slot App Menu | Cause: Application menu Customization conflict error. More than one option slot has requested to customize the application menus 18, 19 and 20. Remedy:
| 204, 209, 214 SlotX Different | Cause: Option module in option slot X has changed. The module installed is a different type to that installed when parameters were last saved. Remedy:
| 202, 207, 212 SlotX Error | Cause: Option module in option slot X has detected an error. Remedy:
| 200, 205, 210 SlotX HF | Cause: Option module X hardware fault. The module cannot operate. Possible causes include module category identification failure, memory allocation issues, or drive failing to read menu tables. Remedy:
| 203, 208, 213 SlotX Not Fitted | Cause: Option module in option slot X has been removed since the last power up. Remedy:
| 201, 206, 211 SlotX Watchdog | Cause: Option module watchdog function service error. The option module started the watchdog function and then failed to service it. Remedy:
| 226 Soft Start | Cause: Soft start relay failed to close, soft start monitor failed. Remedy:
| 221 Stored HF | Cause: Hardware trip has occurred during last power down. A hardware trip (HF01 – HF20) occurred and the drive has been power cycled. Remedy:
| 227 Sub-array RAM allocation error | Cause: The Sub-array RAM indicates that an option module, derivative image or user program image has requested more parameter RAM than is allowed. The RAM allocation is checked in order of resulting sub-trip numbers. Remedy:
| 218 Internal thermistor has failed | Cause: The Temp Feedback trip indicates that an internal thermistor has failed. The thermistor location can be identified by the sub-trip number (e.g., Control PCB, Power system). Remedy:
| 10 Brake resistor over temperature | Cause: Hardware based braking resistor thermal monitoring is connected and the resistor overheats. If the braking resistor is not used then this trip must be disabled with bit 3 of Action On Trip Detection (10.037). Remedy:
| 25 Motor thermistor short circuit | Cause: The motor thermistor connected to the drive is short circuit or low impedance (i.e. < 50 Ω). Remedy:
| 24 Motor thermistor over-temperature | Cause: The motor thermistor connected to the drive has indicated a motor over temperature. Remedy:
| 110 Drive has tripped and the cause of the trip is Undefined | Cause: The power system has generated but did not identify the trip. The cause is unknown. Remedy:
| 249 On board user program error | Cause: An error has been detected in the onboard user program image. The reason is identified by the sub-trip number (e.g., Divide by zero, Undefined trip, Array bounds violation, etc.). Remedy:
| 96 Trip generated by an onboard user program | Cause: This trip can be initiated from within an onboard user program using a function call which defines the sub-trip number. Remedy:
| 36 User Save error / not completed | Cause: An error has been detected in the user save parameters saved in non-volatile memory. Can happen if power is removed while parameters are being saved. Remedy:
| 40 – 89 112 – 159 User generated trip | Cause: These trips are not generated by the drive and are to be used by the user to trip the drive through an application program. Remedy:
| 169 Supply voltage out of range detected in Regen mode | Cause: Regen Minimum Voltage (03.026) is set to a non-zero value and the supply voltage is outside the range defined by Min/Max parameters for more than 100 ms. Remedy:
| 30 Control word watchdog has timed out | Cause: The control word has been enabled and has timed out. Once Pr 06.042 bit 14 has been changed from 0 to 1 to enable the watchdog, this must be repeated every 1s or a Watchdog trip will be initiated. Remedy:
| Error 1 Programming Memory Error | Cause: There is not enough drive memory requested by all the option modules. Remedy: Power down drive and remove some of the option modules until the message disappears. |
| Error 2 Option Module Error | Cause: At least one option module did not acknowledge the reset request. Remedy: Power cycle drive. |
| Error 3 Boot Loader Erase Failure | Cause: The boot loader failed to erase the processor flash. Remedy: Power cycle drive and try again. If problem persists, return drive. |
| Error 4 Boot Loader Program Failure | Cause: The boot loader failed to program the processor flash. Remedy: Power cycle drive and try again. If problem persists, return drive. |
| Error 5 Option Module Init Failure | Cause: One option module did not initialize correctly. Option module did not set Ready to Run flag. Remedy: Remove faulty option module. |
| Brake Resistor Brake Resistor Overload | Cause: Braking Resistor Thermal Accumulator (10.039) in the drive has reached 75.0 % of the value at which the drive will trip. Remedy: Check braking resistor sizing or reduce braking duty cycle. |
| Motor Overload Motor Protection Warning | Cause: Motor Protection Accumulator (04.019) in the drive has reached 75.0 % of the value at which the drive will trip and the load on the drive is > 100 %. Remedy: Check motor load and dwell times. |
| Ind Overload Regen Inductor Overload | Cause: Inductor Protection Accumulator (04.019) in the drive has reached 75.0 % of the value at which the drive will trip and the load on the drive is > 100 %. |
| Drive Overload Drive Over Temperature | Cause: Percentage Of Drive Thermal Trip Level (07.036) in the drive is greater than 90 %. |
| Auto Tune Autotune Active | Cause: The autotune procedure has been initialized and an autotune in progress. |
| Limit Switch Limit Switch Active | Cause: Indicates that a limit switch is active and that is causing the motor to be stopped. |
| Inhibit Drive Inhibited | Cause: The drive is inhibited and cannot be run. The Safe Torque Off signal is not applied to Safe Torque Off terminals or Pr 06.015 is set to 0. (Output Stage: Disabled) |
| Ready Drive Ready | Cause: The drive is ready to run. The drive enable is active, but the drive inverter is not active because the final drive run is not active. (Output Stage: Disabled) |
| Stop Stopped | Cause: The drive is stopped / holding zero speed. (Output Stage: Enabled) |
| Run Running | Cause: The drive is active and running. (Output Stage: Enabled) |
| Scan Synchronizing | Cause: The drive is enabled in Regen mode and is trying to synchronize to the supply. (Output Stage: Enabled) |
| Supply Loss Supply Loss Detected | Cause: Supply loss condition has been detected. (Output Stage: Enabled) |
| Deceleration Decelerating | Cause: The motor is being decelerated to zero speed / frequency because the final drive run has been deactivated. (Output Stage: Enabled) |
| dc injection DC Injection Braking | Cause: The drive is applying dc injection braking. (Output Stage: Enabled) |
| Position Position Control Active | Cause: Positioning / position control is active during an orientation stop. (Output Stage: Enabled) |
| Trip Drive Tripped | Cause: The drive has tripped and no longer controlling the motor. The trip code appears in the lower display. (Output Stage: Disabled) |
| Active Regen Active | Cause: The regen unit is enabled and synchronized to the supply. (Output Stage: Enabled) |
| Under Voltage Under Voltage State | Cause: The drive is in the under voltage state either in low voltage or high voltage mode. (Output Stage: Disabled) |
| Heat Motor Pre-heat | Cause: The motor pre-heat function is active. (Output Stage: Enabled) |
| Phasing Phasing Test | Cause: The drive is performing a ‘phasing test on enable’. (Output Stage: Enabled) |
| Booting Parameters Loading Parameters | Cause: Parameters are being loaded. Drive parameters are being loaded from an SD Card. |
| Booting User Program Loading User Program | Cause: User program is being loaded from an SD Card to the drive. |
| Booting Option Program Loading Option Program | Cause: User program is being loaded from an SD Card to the option module in slot X. |
| Writing To NV Card Writing Data | Cause: Data is being written to an SD Card to ensure that its copy of the drive parameters is correct because the drive is in Auto or Boot mode. |
| Waiting For Power System Waiting for Power Stage | Cause: The drive is waiting for the processor in the power stage to respond after power-up. |
| Waiting For Options Waiting for Option Module | Cause: The drive is waiting for the Options Modules to respond after power-up. |
| Uploading From Options Updating Database | Cause: Loading parameter database. At power-up it may be necessary to update the parameter database held by the drive because an option module has changed. |
How to Read M754 Faults via Connect & Machine Control Studio
In 2026, troubleshooting the M754 requires two primary software tools because of its dual-processor architecture.
- Connect Software (Drive Diagnostics): Use the Connect tool via the onboard Ethernet ports to diagnose hardware trips. The Trip Log (Menu 10) stores the last 10 events. You can view “freeze-frame” data capturing torque and speed at the millisecond of the trip.
- Machine Control Studio (Motion Diagnostics): If you encounter a “User Trip” or a “Controller Trip,” you must use **Machine Control Studio** (based on CODESYS). This allows you to log into the internal MCi processor to check for runtime errors, divide-by-zero errors, or array index issues in your motion code.
- Dual Port Ethernet: Use the onboard Ethernet ports to monitor both the drive parameters (via Modbus TCP) and the motion controller status simultaneously.
- Onboard PLC Log: The M754 maintains a separate system log for the MCi controller. If the drive is running but the motion logic stops, check Menu 11 for internal PLC status bits.
Q: What is a “User Trip” on the M754?
A: A User Trip is a custom fault triggered by the internal MCi program. Developers often program these to trigger when a mechanical safety is breached or a process limit (like a jam) is detected. To find the cause, you must look at the source code in Machine Control Studio.
Q: How do I reset a Digitax HD M754 fault?
A: Once the root cause is resolved, you can reset the drive via:
- Pressing the Red STOP/RESET button on the keypad (if installed).
- Cycling the Main Power (Wait for the display to turn off fully).
- Sending a Reset Command via the PLC program or Ethernet network.
- Toggling a Digital Input assigned to the “Reset” function (Parameter 10.033).
Q: What does “inh” (Inhibit) mean?
A: “inh” is a status code, not a fault. It indicates that the Safe Torque Off (STO) circuit is open. On the M754, this prevents the motion controller from enabling the motor. Check your safety relays and E-stop circuit.
Q: My drive shows “Enc1,” what does that mean?
A: This is a Primary Encoder Fault. It means the motor position feedback has been lost or corrupted. Inspect the encoder cable for damage and ensure the connector is securely fastened at the motor end.
Q: Where is the trip history stored?
A: The trip history is stored in non-volatile memory in Menu 10. Parameter 10.020 always holds the most recent trip. Even if the MCi processor is rebooted, the hardware trip log remains intact.