F021 fault in WEG CFW900 Drive
F021 fault in WEG CFW900 Drive indicates a DC Link Undervoltage. This means the internal DC bus voltage has dropped below the safe operating minimum, usually due to an input power dip.
Supply voltage is too low, producing voltage on the DC link (S2.7.1) below the minimum value:
  • Ud < 203 V: Supply voltage 200 V.
  • Ud < 210 V: Supply voltage 208-240 V.
  • Ud < 385 V: Supply voltage 380 V.
  • Ud < 405 V: Supply voltage 400-415 V.
  • Ud < 446 V: Supply voltage 440-460 V.
  • Ud < 487 V: Supply voltage 480 V.
  • Ud < 507 V: Supply voltage 500-525 V.
  • Ud < 557 V: Supply voltage 550-600 V.
  • Ud < 669 V: Supply voltage 660-690 V.
  • Phase loss at the input.
  • Fault on the pre-charge circuit.
  • Parameter C1.1.2 is configured with a value above the rated line voltage.
Verify incoming mains supply. Check input terminals and check for missing phases. Check the pre-charge circuit. Verify the configuration value of parameter C1.1.2.